TPO Roof
October 28, 2026 at 2:50 p.m.
Bob from PA asks:
I had a Tpo roof installed yesterday. It was adhered to a 1 inch iso board using Lvoc bonding agent. There are quite a few bubbles on the roof. The roofer is telling me that this is normal and will flatten out. I’m not too sure and wanted to get some others opinions. Thank you.
October 28, 2026 at 2:55 p.m.
Bob, based on the photos, this looks like the low-VOC bonding adhesive may have been applied a little heavily, or the membrane was installed before the adhesive had fully flashed off. That can trap solvent and cause the bubbles you are seeing. I cannot confirm the exact cause from photos alone, but I have seen this condition before.
The manufacturers treat low-VOC adhesives differently from some of their standard bonding adhesives. With certain low-VOC systems, their guidance is to let trapped solvent dissipate naturally for four to five days, then have the contractor return and thoroughly re-broom the membrane so it lies flat.
That makes your roofer’s explanation reasonable, but follow-through matters. I would expect the contractor to return after that period, re-broom the affected areas, and verify that the membrane is properly bonded. I would not recommend trying to broom or repair it yourself.
This condition does not automatically mean the roof will leak, especially if the membrane and welded seams are sound. The main concern is whether the bubbles settle and bond after the solvent dissipates or whether some areas remain dry and unbonded.
I recommend documenting the roof with dated photos and confirming the exact adhesive used. If the bubbles remain after the contractor re-brooms the roof, ask the membrane manufacturer’s technical department to review the condition and confirm whether any additional work is needed or whether the warranty could be affected.